100 cubic methanol storage tank design
If the feed pump and high alarm from the security consideration are not only a chain, but also a security instrument system The connection between the jar should be used to avoid sinking damage.The import and export of the jar should be added with an emergency cutting valve (FC), if the fire is cut off as soon as possible.
If the feed pump and high alarm from the security consideration are not only a chain, but also a security instrument system The connection between the jar should be used to avoid sinking damage.The import and export of the jar should be added with an emergency cutting valve (FC), if the fire is cut off as soon as possible.
The nitrogen required for nitrogen sealing facilities is foreseeable, and the consumption will not be too large. I think it is impossible to use nitrogen cylinders as a nitrogen source.At present, these flammable and explosive storage tanks are required to add nitrogen sealing facilities.
The nitrogen required for nitrogen sealing facilities is foreseeable, and the consumption will not be too large. I think it is impossible to use nitrogen cylinders as a nitrogen source.At present, these flammable and explosive storage tanks are required to add nitrogen sealing facilities.
From the experience I designed and the feedback of the owner, it is recommended to change the insulation in water and cool down;It is necessary to use it, it will be much better, which is mainly reflected in the production environment. In addition, the volume of breathing will be reduced a lot. If the amount of gas is seal will be used, the amount of gas will come down.High -level links can not be available, but it is recommended to increase the high liquid level switch. This investment is not large and can effectively avoid liquid leakage; setting the fire embankment, the embankment accumulation can collect the outflow of the liquid;; Pay attention to explosion -proof and qualify for lightning protection for lighting; this volume storage tank on fire facilities can use mobile foam, throwing the connection from the upper part of the tank, the pressure of the outdoor fire hydrant can meet the mobile foam fire extinguishingRequire.
From the experience I designed and the feedback of the owner, it is recommended to change the insulation in water and cool down;It is necessary to use it, it will be much better, which is mainly reflected in the production environment. In addition, the volume of breathing will be reduced a lot. If the amount of gas is seal will be used, the amount of gas will come down.High -level links can not be available, but it is recommended to increase the high liquid level switch. This investment is not large and can effectively avoid liquid leakage; setting the fire embankment, the embankment accumulation can collect the outflow of the liquid;; Pay attention to explosion -proof and qualify for lightning protection for lighting; this volume storage tank on fire facilities can use mobile foam, throwing the connection from the upper part of the tank, the pressure of the outdoor fire hydrant can meet the mobile foam fire extinguishingRequire.
Just find the regular design institute for your design institute. You asked the east and west, and finally find a design unit to set a picture to sign the picture.So messy
Just find the regular design institute for your design institute. You asked the east and west, and finally find a design unit to set a picture to sign the picture.So messy
After reading a lot of discussions and suggestions above, it has been very complete. Personal suggestions, nitrogen seals still have to be available.The tank should also set the corresponding setting nitrogen leakage system to avoid over pressure.This nitrogen sealing system is relatively complicated.
After reading a lot of discussions and suggestions above, it has been very complete. Personal suggestions, nitrogen seals still have to be available.The tank should also set the corresponding setting nitrogen leakage system to avoid over pressure.This nitrogen sealing system is relatively complicated.
The connection between the jar should be used to avoid sinking damage.The import and export of the jar should be added with an emergency cutting valve (FC), if the fire is cut off as soon as possible.
The connection between the jar should be used to avoid sinking damage.The import and export of the jar should be added with an emergency cutting valve (FC), if the fire is cut off as soon as possible.
VOTE
VOTE
VOTE
Putting nitrogen seal, safety valve or bleaching human hole.
Putting nitrogen seal, safety valve or bleaching human hole.
VOTE
VOTE
VOTE
High liquid level alarm and unloading pump pump lock device.
High liquid level alarm and unloading pump pump lock device.More